Builder Forum Series: Ventilation and Step Code Presented by TOL Green Buildings and Focal Engineering
Builder Forum Series:
Ventilation and
Step Code
Presented by TOL Green Buildings
and Focal Engineering

                     Wednesday, January 27, 2021
                                 9:00 – 10:30 am
Builder Forum Series: Ventilation and Step Code Presented by TOL Green Buildings and Focal Engineering
Reminders / Updates
AGENDA
         •
         •   Live Polling
         •   Ventilation and Step Code
         •   Closing

         • Mentimeter poll coming up soon!
         • Go to menti.com and use the code 26 97 57
Builder Forum Series: Ventilation and Step Code Presented by TOL Green Buildings and Focal Engineering
November
BFS Recap
• Air Tightness
   •   Step Code – ACH targets
   •   Plan from the START
   •   Work with trades
   •   Mid-construction testing
• Heat Pumps
   • Important for meeting Upper Steps
   • Understand heat pump’s recommended operations
   • Holistic design is critical

                                  • Mentimeter poll coming up soon!
                                  • Go to menti.com and use the code 26 97 57
Builder Forum Series: Ventilation and Step Code Presented by TOL Green Buildings and Focal Engineering
tol.ca/stepcode
Builder Forum Series: Ventilation and Step Code Presented by TOL Green Buildings and Focal Engineering
Builder Forum Series: Ventilation and Step Code Presented by TOL Green Buildings and Focal Engineering
Reminders
• 2021
   • GHG DPA - Step 3 is required
   • NON-GHG DPA - Step 2 is compliant
• 2022
   • GHG DPA – Step 3 is required
   • NON-GHG DPA – Step 3 is required
• 2022 – onwards
   • Tracked results will inform future
     adoption
Builder Forum Series: Ventilation and Step Code Presented by TOL Green Buildings and Focal Engineering
BP Submissions
Make sure you submit all documents

• Easy for us to review
• Fewer requests for documentation

tol.ca/stepcode
                               • Mentimeter poll coming up soon!
                               • Go to menti.com and use the code 26 97 57
Builder Forum Series: Ventilation and Step Code Presented by TOL Green Buildings and Focal Engineering
Documentation for Step Code Part 3 BP application

• BC Energy Intensity Report – Completed and Signed by P.Eng.
• Part 3 Energy Design report
• Calculations or analysis showing effective building envelope performance
  including thermal bridging.
• Energy Modeling Report                            Recommended reference
                                                    Whole Building Energy modeling
• Energy Statement on drawings                      services guideline by AIBC

                                         • Mentimeter poll coming up soon!
                                         • Go to menti.com and use the code 26 97 57
Builder Forum Series: Ventilation and Step Code Presented by TOL Green Buildings and Focal Engineering
Remember!!
All Energy Analysis in Langley – Use Abbotsford Weather file

Part 9 buildings in Langley:
- Use the latest version of BC Energy compliance report
- Use HDD 2700 for TEDI calculations
- Section F of Compliance form is now required to be completed.

For Part 3 Passively Cooled Buildings
 - Refer to ASHRAE 55-2010 as per Vancouver Modeling Guidelines.
 - Use Abbotsford Weather file (2016_CAN_BC_ABBOTSFORD-A_1100031_CWEC)

                                        • Mentimeter poll coming up soon!
                                        • Go to menti.com and use the code 26 97 57
Builder Forum Series: Ventilation and Step Code Presented by TOL Green Buildings and Focal Engineering
NEW Incentives
       • Significant new construction
         incentives
       • Focuses on
           • Upper Steps
           • Heat pumps
           • Electrification
       • CAN combine with GBRP

• Mentimeter poll coming up soon!
• Go to menti.com and use the code 26 97 57
NEW Incentives
• Mentimeter poll coming up soon!
• Go to menti.com and use the code 26 97 57
Upcoming Builder Forum
• Fenestration and Building
  Performance
   • Cost effective high performance
     fenestration solutions
   • Fenestration and thermal comfort
   • Lessons learned and examples of
     design/install
• Aiming for March 23rd

                                        Credit: RDH Building Science Passive House Pattern Language
City of Abbotsford upcoming Step Code Cafe
COMING SOON!
Part 3 Non-Res Step Code
• Consultation coming soon
• Keep eyes open for email
• We appreciate your input
Climate Action Strategy (CAS)
• Unanimously Approved by Council Jan 25th, 2021
• Buildings are a large chunk of the C02 portfolio
• Anticipate buildings policy aligning with CAS
Mentimeter
time!
Go to menti.com and use
code 26 97 57
NOVEMBER 19 BUILDER FORUM
SERIES: WHAT WE HEARD FROM YOU                      Has your airtightness knowledge
                                                                                                     “Mid-construction blower door tests are
                                                    increased?                                       an excellent way to correct weaknesses in
 Level of satisfaction with the webinar:                          52%                                the air barrier at an early stage“
                      Somewhat                         26%
  Somewhat                                                                   23%
  Satisfied 10%    3% Dissatisfied
                                                                                         0%          “Seeing how [airtightness] testing was
                                                                                                     carried out helped with understanding
                                                   Stayed the Increased Increased    Not             what is required to make the building
                                                      same       a bit    greatly applicable         airtight.“
                               Satisfied
                   87%
                                                   Has your heat pump knowledge                     Has the webinar increased your
  “I would like to see more about cost issues. I   increased?                                       confidence in building to the Upper
  have heard a lot of comments from perspective                   68%                               Steps of the Step Code?
  buyers who have purchased used houses
                                                                                                       Increased 19%                   Stayed the
  because of new construction costs.”                  16%                   16%                                                19% same
                                                                                        0%             greatly
  Any fears or concerns building to
                                                    Stayed the Increased Increased    Not
  Upper Steps?
                                                       same       a bit    greatly applicable
       No fears/concerns      6%                                                                                         61%
       Failing inspections         29%             “I was happy to hear the message presented         Increased a
                                                   (strongly) that the air barrier is made up of      bit
 Trades are inexperienced                  65%
                                                   many components, and that the various
   Not meeting deadlines        19%
                                                   tradespeople have a responsibility in ensuring
          Increased costs                  61%     the air barrier’s integrity […]“
FOCAL Engineering
• Mechanical engineer with over 15 years of
  industry experience
• Sits on several code committees related to
  energy modelling and the BC Step Code.
• A principal at Focal Engineering –Energy
  efficiency, new construction and retrofit
Builder Forum Series:
Ventilation & Step Code
WES BOWLEY, E.I.T / SUSAN MACDOUGALL, P.ENG.
JANUARY 27, 2021

                                               Building. Performance.
Introduction

Agenda   Step Code Overview
         Ventilation Overview
         Ventilation & Step Code
         Key Design Strategies
         Other Design Considerations
         Conclusion
Purpose   Focus on Part 9 & Part 3 residential buildings
          Discuss how ventilation impacts Step Code compliance
          and various metrics
          Present successful, cost-effective design strategies and
          tips to achieve Step Code
Step Code
Stepped Approach

                           From BC Energy Step Code:
                           A Best Practices Guide for Local Governments
                           www.energystepcode.ca

© Focal Engineering Inc.
Step Code Metrics
                                                                      Overheating

                                                                            n/a

                                                                      Passively-cooled
                                                                         Buildings

                           Definitions
                           • MEUI = Mechanical Energy Use Intensity
                           • TEUI = Total EUI
                           • TEDI = Thermal Energy Demand Intensity

© Focal Engineering Inc.
Ventilation
Ventilation Overview
    Outdoor airflow requirement in buildings
      ◦ Typically in occupied spaces
      ◦ Other reasons (e.g. pollutants, such as parkades)

    Outdoor Air (O/A) delivered to & Exhaust Air (E/A) from spaces
      ◦ Usually described as flow rate, i.e. air volume over period of time

    Typically mechanical
      ◦ Can also be passive (e.g. windows)

    Can impact
      ◦ Energy consumption
      ◦ Thermal comfort
      ◦ Envelope performance

© Focal Engineering Inc.
Residential Ventilation
    Typically O/A or E/A requirement for:
      ◦ The home, or each suite in a MURB
      ◦ Common spaces (e.g. corridors, amenity, mech rooms, parkade)

    Older strategies used exhaust only
      ◦ Bathroom & kitchen fans
      ◦ Downside = can’t control incoming air
         ◦ Would leak in through envelope (potential issues)
         ◦ Can’t pre-heat

    Move towards balanced ventilation, supply & exhaust
      ◦ Opportunity to add heat recovery
      ◦ Can filter incoming air; better indoor air quality & more resilience (e.g. smoke events)

© Focal Engineering Inc.
BC Building Code 2018 Rev2
    Ventilation requirements in BC, references some other documents/ standards (noted with    )

                                           ASHRAE 62-2001

                 Division B, 6.3
                   Ventilation
                    Systems                                          Flow rate requirements
                                                 9.32
                                      Housing and Small Buildings
                                              Ventilation
                                                                       CAN/CSA F-326-M

© Focal Engineering Inc.
Other Standards

      ASHRAE 62.1-2001                                CAN/CSA F-326

      Ventilation for Acceptable Indoor Air Quality   Residential Mechanical Ventilation Systems
      ◦ Applies to all buildings/ spaces              ◦ Ventilation for in the home/ suite
         ◦ Corridors included
         ◦ Generally not used within homes/ suites

© Focal Engineering Inc.
Step Code Buildings
    A few extra rules for Step Code Buildings…

                                       ASHRAE 62-2001               Flow rate requirements

            Division B, 6.3                  9.32
              Ventilation         Housing and Small Buildings         CAN/CSA F-326-M
               Systems                    Ventilation

                                    6.3.1.1(4) O/A must be       9.32.3.4(6)(iv) O/A can not be
                                  mechanically ducted to each       passively supplied from
                                   suite (can not be indirect)             outdoors

© Focal Engineering Inc.
Some organizational requirements
    Example: BC Housing
    Central HRV flow rate requirements for
      ◦ Based on # of bedrooms

    In-suite HRV flow rate requirements
      ◦ Based on # of bathrooms

    Also require minimum 75% sensible heat recovery

© Focal Engineering Inc.
Example Projects
Part 9: Single Family Home
    Step 5 (Passive House)
    Saanich, BC (HDD 2650)
    Area: 188 m2 (2020 ft2)
    Bedrooms: 3
    Bathrooms: 2

© Focal Engineering Inc.
Part 3: Multi-Unit Residential Building
    Step 2 MURB
    Victoria, BC (HDD 2750)
    5 floors
      ◦ 1 concrete
      ◦ 4 wood-framed

    72 suites plus amenity
    Area: 3,952 m2 (42,500 ft2)

© Focal Engineering Inc.
Ventilation & Step Code
Step Code & Ventilation
    How does ventilation impact step code?
                                                                    Overheating

                                                                          n/a

                                                                    Passively-cooled
                                                                       Buildings

    Biggest impact on TEDI
    Our residential strategy: focus on TEDI and MEUI/ TEUI passes

© Focal Engineering Inc.
Impact on TEDI
                                                                         Step 2 MURB
                                                    Glazing, 7.1
                                                                          ◦ TEDI requirement = 45 kWh/m2/year

  Ventilation,
     17.6
                                                                         Compare the big 3 losses
                           17.6                   16.9      Walls, 5.5
                                                                          ◦   Ventilation
                                    43.5
                                                                          ◦   Envelope- Infiltration
                                                                          ◦   Envelope- Assemblies
                                                            Roof, 1.9     ◦   Ventilation ~40% of TEDI
                                      8.9
                                                         Floor, 2.2

                                                         Door, 0.2       Typically, ventilation ~25-50%
                                  Infiltration,                           ◦ For step code projects that pass
                                       8.9                                ◦ Generally lower for higher steps

© Focal Engineering Inc.
Impact on MEUI/TEUI
    Step 2 MURB
      ◦ TEUI Requirement = 130 kWh/m2/year

                             Result                                                           123.7

                              Step                            4                          3     2

                                      0   10   20   30   40   50 60 70 80        90 100 110 120 130
                                                              TEUI (kWh/m²/yr)

                           Ventilation impacts

© Focal Engineering Inc.
Adjustment: Corridor Pressurization
    Part 3 Corridor pressurization adjustment
      ◦   Accounts for local, typical practice of over-ventilation
      ◦   Reduces TEDI/ TEUI
      ◦   Limited to adjustment of 10 kWh/m2/year
      ◦   Can have a big impact, especially on higher steps

    Calculation based on
                                                                                   Vancouver Energy
      ◦   Pressurization airflow
                                                                                      Modelling
      ◦   Corridor area                                                               Guidelines
      ◦   Modelled building area                                                     Section 2.5.2
      ◦   # units
      ◦   HDD                                                        Available at: https://vancouver.ca/files/cov/
                                                                                   guidelines-energy-modelling.pdf

© Focal Engineering Inc.
Example: Step 2 MURB
    Comparing ASHRAE 62.1-2001 ventilation rate to actual design

                                                                   Step 2 MURB (totals for 5 floors)
                 Corridor Area [m2]                                              298
                 ASHRAE 62            Ventilation Flow Rate          74.5 L/s          160 CFM
                                      Ventilation per Suite Door      1.0 L/s            2 CFM
                 Actual Design        Ventilation Flow Rate          320 L/s           680 CFM
                                      Ventilation per Suite Door      4.4 L/s            9 CFM

© Focal Engineering Inc.
Example: Step 2 MURB
    TEDI requirement = 45 kWh/m2/year
    Project before adjustment
      ◦ TEDI = 48.4 kWh/m2/year
      ◦ Fails

    Corridor Adjustment calculated as 4.8
    Project after adjustment
      ◦ TEDI = 43.6 kWh/m2/year
      ◦ Passes

    Note
      ◦ Only on pressurization airflow
      ◦ If 150 CFM supplied to corridor and 50 CFM exhausted,
        adjustment will only apply to 100 CFM

© Focal Engineering Inc.
Key Strategies
Strategy 1: Don’t over ventilate
    Applied to: all spaces

    May seem obvious, but rates easily creep up with:
      ◦   Conservative calculations
      ◦   Safety factor/ rounding up
      ◦   Selecting larger equipment
      ◦   Testing/ balancing/ commissioning (more later)

© Focal Engineering Inc.
Strategy 2: Heat recovery
    Pretty much every step code project we see has heat recovery
    Suggested target efficiencies
      ◦ Remember some organizational requirements (e.g. BC Housing min. 75%)

    Part 3                                          Part 9
      ◦ Step 2: 60-70+%                              ◦   Step 2: 60+%
      ◦ Step 3: 70-80+%                              ◦   Step 3: 60-70+%
      ◦ Step 4: 80-90+%                              ◦   Step 4: 70-80+%
                                                     ◦   Step 5: 80-90+%

© Focal Engineering Inc.
Example: Step 2 MURB                                             Heat
                                                                   Recovery

    Graph on right compares gains/ losses that
    contribute to TEDI                             Ventilation

                                                                   Fan Heat
                                                                    Pickup
    Remember Step 2 MURB TEDI was ~40%
                                                                    Plugs
    from ventilation?
      ◦ That’s after heat recovery                                Occupants

                                                                   Lighting
                                                   Infiltration   Solar Gains
    Ventilation is biggest loss
                                                     Doors
      ◦ Only reduced to 40% because of H/R           Floor
                                                     Roof
      ◦ Note: graph shows more H/R opportunities     Walls          Heating
        available                                   Skylight
                                                                  Load (TEDI)

                                                    Glazing

                                                    Losses          Gains

© Focal Engineering Inc.
Strategy 3:
    MURBs Central versus Local
     LOCAL (IN-SUITE)                                          CENTRAL

     Pros                                                      Pros
       ◦   Easier to bill each suite                           ◦ Less maintenance (single unit/ filter, etc.)
       ◦   Less floor area lost to shafts between floors       ◦ Fewer penetrations through the envelope
       ◦   No fire/ smoke dampers                              ◦ Possibly fewer dropped ceilings in suites
       ◦   Individual suite control (i.e. easier to increase
           when cooking/ showering/ etc.)
                                                               Con
                                                               ◦ Providing individual control is expensive
                                                                 requiring costly pressure sensors…
                                                                 one solution on next slide

© Focal Engineering Inc.
Strategy 3:
    Overcoming Central Control Challenge
    Instead of running :                                  Size HRV system for 65%
      ◦ HRV at 60% continuous                              ◦ Run continuously
      ◦ Bump up airflow 3 hrs/day to 100% for              ◦ Better consistent air quality
        showers, cooking, etc.

                                      Ventilation Central Control Solution
       1
                                                                             Continous 60%, with 100% bump
    0.8                                                                      Continous, 65%
    0.6
    0.4
    0.2                                                                           Same daily airflow
       0
           1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24

© Focal Engineering Inc.
Strategy 4: Corridors
    Reduce air volumes
      ◦ If adjustment is over the limit of 10, corridors likely over-ventilated

    Add/ improve heat recovery
      ◦ Remember this will impact the corridor adjustment if not pressurizing space
      ◦ Option: Pre-heat with central HRV but don’t return air; still pressurizes space

    Reduce heating setpoint temperatures
      ◦ For example, could heat to 18°C instead of 20°C in winter

    Consider external corridors
      ◦ No ventilation required
      ◦ Needs to be planned early on
      ◦ Use caution: Other implications (reduces area for TEDI & other calcs, lose adjustment, etc.)

© Focal Engineering Inc.
Strategy 5: Achieving highest steps
    Common strategy seen on most PH projects can be adapted for higher steps
    Step 5 (PH) Home example
    HRV
      ◦ Supply to living spaces (bedrooms, living room, etc.)
      ◦ Exhaust from bathrooms, kitchen
      ◦ Run continuously = good IAQ
    Bathroom
      ◦ Controls for balanced increase in supply & exhaust
    Kitchen
      ◦ Constant exhaust
      ◦ Recirculating hood with
         ◦ Mesh filter for water vapour
         ◦ Charcoal filter for odour removal

© Focal Engineering Inc.
Other Considerations
HRV versus ERV
    HEAT RECOVERY VENTILATION                     ENERGY RECOVERY VENTILATION

    Sensible heat recovery only                   Sensible & latent heat (moisture transfer)
                                                  recovery
    Good for Lower Mainland in most
    applications                                  Can prevent air from getting too dry in
                                                  winter (more for cold climates)
    Moisture buildup on cold days requires
    condensate drain (additional plumbing)        Not allowed in some sensitive applications
                                                  due to potential particle transfer

   Note: Both realize benefits of better energy efficiency & IAQ over exhaust-only

© Focal Engineering Inc.
Commissioning, TAB, Maintenance
    In real life, construction & operation will impact utility bills

    Important to test, balance, commission, system to match design
      ◦ Check airflows are correct, in the space & at the unit
      ◦ Test HRV/ERV
         ◦ At low (continuous) and high rates
         ◦ In bypass mode

    Provide manual to owners
      ◦ Explaining: bypass mode, preheat (if applicable), etc.
      ◦ How frequently should filters be changed
      ◦ Other maintenance considerations

© Focal Engineering Inc.
Commercial buildings
    For Step Code, this means: office, retail, hotel buildings & public sector buildings (step 1)
    Also amenity spaces within MURBs

          Same strategies as             Demand Control                 Sub-meter energy
               before                      Ventilation                       usage
         • Don’t over ventilate       • Only provides outdoor air     • Helpful to the building
         • Use heat recovery            when needed                     owner
         • Lower heating setpoint,    • Useful in spaces with         • Can track actual building
           where possible               varied usage (e.g.              use to realize true
                                        amenity rooms)                  energy/ cost savings
                                      • Commercial kitchens,
                                        separate make-up air
                                        with efficient heating

© Focal Engineering Inc.
GHGI reduction opportunities
    Strategies to reduce TEDI and MEUI/ TEUI will generally
    reduce GHGI

                                                                             GHG
    Also consider:                                                         Emissions
      ◦ If using gas, highest efficiency units (condensing over regular)
      ◦ Switching fuel from gas to electric
         ◦ Corridor makeup air units
         ◦ Boilers & backup boilers for hydronic heating systems
           (costing comes in cheaper than gas)
         ◦ Note: Could have impact on electrical service
      ◦ Renewables

© Focal Engineering Inc.
Conclusion
Key Takeaways
                           ◦ TEDI is the hardest Part 9 & 3 metric to meet
                            ◦ Ventilation is one of the big 3 contributors (remember the donut!)
                            ◦ Reducing the ventilation portion is an easy win

                           ◦ Addressing TEDI will improve MEUI/ TEUI & GHGI

                           ◦ Strategies
                            ◦   Don’t over ventilate (design and controls)
                            ◦   Use good heat recovery
                            ◦   Consider special strategies for corridors, unique spaces & higher steps
                            ◦   Build well, balance, commission & maintain

© Focal Engineering Inc.
Additional Resources
    Energy Step Code Website, www.energystepcode.ca

    Part 9 Handbook for Building Officials
      ◦ Has section on ventilation with design examples

    Part 3 Energy Design Report
      ◦ Includes corridor adjustment calculator

    Part 3 Step Code Design Guide & Supplement
      ◦ Sections on Ventilation system & strategies

© Focal Engineering Inc.
Thank you!
susan@focaleng.com
10 minutes for Q+A
Credits
• BC Housing CPD - We will send you the proof of attendance. Your
  registration/sign-in today acts as your proof
• AIBC - No work on your part!
• Attendance is tracked – One credit per hour
• Sarah will send the attendee list to AIBC and they will give you your
  LUs
Acknowledgements
• Susan MacDougall, Wes Bowley FOCAL - susan@focaleng.com
• BC Hydro

                 Thank you
• FortisBC
• YOU!
Greenbuildings@tol.ca
tol.ca/greenbuildings
You can also read